dvanlanen
Posted: Thu Apr 10, 2008 7:23 am Post subject: Shunts |
I am reading through the AeroElectric Connection manual as I have time, but I am having trouble comprehending some of the concepts presented. I just read about the use of shunts in an electrical system to allow the measurement of large currents with small meters. One thing I don’t understand is, if a shunt is used in the circuit to be measured, what prevents a reduction in energy in the circuit on the downstream side of the shunt? Can someone help me better understand this?
Dave Van Lanen
601XL – Tail [quote][b]
dan(at)familybrown.org Guest
Posted: Thu Apr 10, 2008 7:50 am Post subject: Shunts |
Quoting Dave VanLanen <davevanlanen(at)sbcglobal.net>:
Quote: | understand is, if a shunt is used in the circuit to be measured, what
Nothing prevents it; there is in fact such a reduction. However, it's
such a minuscule reduction that it's not noticeable in ordinary
operation. A shunt typically is designed for a 50 mV voltage drop at
full capacity. So, a 100A shunt will cause a 50 mV drop at 100A. In
a 14V circuit, 100A represents 1400W, and the shunt will consume 5W of
that.
Dan Brown, KE6MKS, dan(at)familybrown.org
"Since all the world is but a story, it were well for thee to buy the
more enduring story rather than the story that is less enduring."
-- The Judgment of St. Colum Cille
mprather(at)spro.net Guest
Posted: Thu Apr 10, 2008 8:32 am Post subject: Shunts |
Hey Dave,
Nothing prevents loss of energy downstream of the shunt. But, a properly
selected shunt will have a relatively small voltage drop at full scale
current - reducing the power consumption of the device. Typical shunts
drop 50mV at full scale. On a 100A peak current circuit that's 5W = 100A
* 50mV. If you figure you're dropping the rest of the 13V supply into the
100A load, you're only losing 5W out of 1300W or 0.3%. Not too terrible.
At lower currents the percentage of power lost is less: 10A through the
same shunt will drop 5mV which is 50mW of the 130W delivered to the load -
or 0.03%.
Many aircraft engine monitors are setup to use Hall Effect sensors - which
do not consume any current from the measured circuit.
Matt-
Quote: | I am reading through the AeroElectric Connection manual as I have time,
but
measurement of large currents with small meters. One thing I don't
the
Dave Van Lanen
601XL - Tail
Posted: Thu Apr 10, 2008 8:33 am Post subject: Shunts |
Hey Dan
That's funny.. We used much of the same verbiage. Even most of the same
example.
Matt-
> the
that.
gmcjetpilot
Posted: Sat Apr 12, 2008 3:38 am Post subject: Shunts |
The AMP meter is really a VOLT METER. Yep it has nothing to do with AMPS. (There is an AMP and VOLT relation).
How does it work. The shunt causes a voltage drop across the shunt (due to resistance). That resistance is a known calibrated value. The volt gauge is reads volt drop. Since voltage drop is proportional to current (amps) the gauge can read the volt drop as current or amps, as follows:
This is the famous OHMS law:
V = I x R
OR
Volts = Current (amps) X Resistance (ohms)
So what?
We know a shunt is "calibrated" to drop a certain volt for every every amp of current. Shunts vary, but a typical 50 amp shunt has a 50 millivolt drop at 50 amps.
If you have 50 amps at 14 volts entering the shunt, the volts leaving the shunt at 50 amps will be 50 millivolts (0.050v) lower or 13.95 volts.
One millivolt drop = one amp. So you need a gauge that is labeled from 0 to 50 amps (but has a range from 0 to 0.050 volts).
With a volt gage that reads millivolts from 0 to 50 millivolts (but labeled amps) we have an AMP METER!
Again the meter is measuring voltage drop not amps. It just happens OHMS LAW is handy and linear (usually); where current and volts are proportional based on the resistance of the shunt.
Shunts can have higher or lower resistance. Not all have the 1 amp to 1 millivolts ratio. That is OK as long as the scale and range of the gauge (analog or digital) compatible or calibrated for that shunt. The 1 amp to 1 millivolt ratio is handy since many volt gauges are calibrated in [quote][b]
echristley(at)nc.rr.com Guest
Posted: Sat Apr 12, 2008 11:06 pm Post subject: Shunts |
gmcjetpilot(at)yahoo.com wrote:
Quote: | The AMP meter is really a VOLT METER. Yep it has nothing to do with AMPS. (There is an AMP and VOLT relation).
Aahh! But is it? Maybe the VOLT meter is really an AMP METER!!
If using a swinging arm type meter, the voltage across the inputs drives
a current that energizes an electromagnet, the forces the deflection.
You're using current to measure a voltage, that's caused by the current
across the shunt, which is caused by a voltage.
Aahiiieee!!
8*)
http://www.ronpaultimeline.com
nuckolls.bob(at)cox.net Guest
Posted: Sun Apr 13, 2008 6:31 am Post subject: Shunts |
At 03:05 AM 4/13/2008 -0400, you wrote:
Quote: |
<echristley(at)nc.rr.com>
Quote: | If using a swinging arm type meter, the voltage across the inputs drives a
Aahiiieee!!
A very astute observation sir. Allowing a coil
of wire to move within the field of a permanent magnet
was the brainchild of a fine fellow named D'arsonval
who conceived the design about 130 years ago. There's
an excellent description of the details of this idea
offered over several pages beginning at:
http://www.tpub.com/neets/book3/7.htm
Hit the "-> next" buttons to access the series.
One may also craft a moving magnet instrument . . .
a good example is Van's ammeter. Unlike the more
fragile and difficult to calibrate moving coil
movement typical of:
http://www.aeroelectric.com/Pictures/Instruments/Loadmeter_2.jpg
Vans ammter shown at:
http://www.aeroelectric.com/Pictures/Instruments/VAM10_Interior_View
moves a barrel shaped magnet in the center of TWO coils
positioned at right angles to each other. This movement
doesn't need springs and is NOT calibrated with respect
to current flowing in the coils. In this case
two coils are excited with a current proportional
to the sine and cosine of the applied stimulus. The magnet
and pointer are often free to rotate 360 degrees. Van's
instrument is "pegged" at -45 amps and has a light spring
that drives the pointer to the peg when the instrument is
powered down. But you could remove the peg and spring.
The pointer would rotate freely and still properly indicate
the mechanical result of the ratio of two currents applied
to the coils. This style of meter movement can be used to
drive something like a compass card for displaying a
heading not unlike that offered by the DG.
This instrument is interesting because it can be
electronically conditioned to display a host of stimuli
and it takes advantage of the full rotational scale
of the instrument. D'arsonval movements get VERY
hard to build beyond 90 to 110 degrees of pointer
swing.
Because they deal with the results of a magnetic
interaction between coil(s) of wire and fixed magnets
both instruments are indeed displays of the effects
of CURRENT.
However, if one considers the internal resistance of
the instrument as being part of the overall circuit,
the raw device can be used to display the effects
of very small voltages. A good example is the classic,
non-amplified CHT instrument. An example is shown
here:
http://www.aeroelectric.com/Pictures/Instruments/CHT%20Gauge.jpg
This puppy reads full scale when something on the order
of 7 MILLIVOLTS is applied to its terminals. This is
the voltage generated by K-type thermocouple wire
at 350F. In this case, the moving coil can be crafted
of few turns of relatively large wire (low resistance)
because while a thermocouple doesn't offer much VOLTAGE,
it is a very low impedance source of energy and can
produce considerable CURRENT at the relatively small
voltage.
All moving coil devices are dependent upon the force
against a spring which is proportional to the current
flowing in a coil of wire. Of course the coil has resistance
of its own so any basic meter movement calibrated for
the measurement of a current may also be said to be
a "voltmeter" . . . typically, rudimentary movements will
indicate full scale with voltages on the order of 10
to 200 millivolts. The instruments designed to work in
conjunction with shunts are generally crafted so that
the CURRENT induced in the coil produces full scale
torque when 50 milliVOLTS (standard shunt calibration)
is applied to the terminals.
Van's instrument is fitted with electronics such that
the stuff sensed at the input terminals is indeed
a voltage . . . the considerable current required
to position the pointer comes from the electronics
power supply and not from the voltage stimuli being
monitored.
I've done some preliminary testing on the Van's
ammeter . . . by modern aviation design goals it
is exceedingly sensitive to local RF fields. I'm
working on an article to explore this condition.
I'll also see if I can craft an easily fabricated
filter or shield as a workaround for this product's
shortcomings.
gmcjetpilot
Posted: Mon Apr 14, 2008 6:13 am Post subject: Shunts |
Oh my my. This is why people make fun of tech geeks and nerds, ha-ha. Yes voltage, current and EMF are all magically intertwined. Even the magic of the hall effect sender puts out proportional volts to current. But you all are right, there are coils in those mechanical gauges. However a digital meter will read directly off a shunt? Huha? What? Doha! ha-ha.
Bob your "VAM10_Interior_View link" is not working?
Cheers
Posted: Mon Apr 14, 2008 7:16 am Post subject: Shunts |
At 07:07 AM 4/14/2008 -0700, you wrote:
Quote: | Oh my my. This is why people make fun of tech geeks and nerds, ha-ha.
Interesting . . . it seems that the same folks would also
make fun of neurosurgeons, master chefs and physicists.
Individuals who poke fun at the assemblage of simple-ideas
into useful inventions are themselves at-risk for not
enjoying the benefits that arise from understanding . . .
a kind of self imposed exile to ignorance that leaves
them dependent upon those who DO understand.
Quote: | Yes voltage, current and EMF are all magically intertwined.
Nothing magic about it. But the conditions under
which they interact are not consistent. For example,
just because there is voltage to be measured doesn't
automatically translate to a current flow. Similarly,
there are conditions where huge magnitudes of current
flow with zero impressed voltage.
Quote: | Even the magic of the hall effect sender puts out proportional
volts to current.
Sort of . . . volts is proportional to the intensity
of a magnetic field. The magnetic field can come from
a variety of sources not the least of which is the
field surrounding a current carrying conductor.
Quote: | But you all are right, there are coils in those mechanical gauges.
Doha! ha-ha.
Yes, the digital voltmeter takes advantage of the
voltage drop impressed across a shunt as a result
of current flow. The measurements obtained by this
method are independent of simple-ideas involving
magnetics.
Quote: | Bob your "VAM10_Interior_View link" is not working?
Yes, I corrected it in the posting that followed
a few minutes after the first. The working link
is . . .
http://www.aeroelectric.com/Pictures/Instruments/VAM40_Interior_View.jpg
( -Thomas Paine 1776- )
