Eric M. Jones



Joined: 10 Jan 2006
Posts: 565
Location: Massachusetts

PostPosted: Wed Nov 20, 2013 2:07 pm    Post subject: Contactors Reply with quote

We have discussed contactors for years and I have always recommended the Kilovac EV200 and the Gigavac GX11, but there is a new contactor available from Gigavac to compete directly with the Kilovac EV200 and offers some additional benefits, such as no noise, terminal shields, and improved performance characteristics. I was considering selling these, but there isn't any meat on the bone left after getting them from Gigavac.

I have one and I like these more than the Kilovacs.

Part Number Description
GX200BB 350A, 12Vdc coil, 24" leads 1-4 $116
5-9 $104
10-24 $99

See: http://www.gigavac.com/pdf/ds/pp/gx200.pdf

(ignore their weird warning to see their other contactors (remember Gigavac is refering to 200A continuous). Gigavac is known for having strange marketing, but great products. Also ignore their manual switches...they are made for really, really, high-voltage applications and are much too big.

But I recommend the GX200 as the best contactor for the task, if you are planning to use a contactor at all.


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net
Back to top
View user's profile Send private message Send e-mail Visit poster's website
jan(at)CLAVER.DEMON.CO.UK
Guest





PostPosted: Wed Nov 20, 2013 2:38 pm    Post subject: Contactors Reply with quote

Hi Eric,

I hope they have improved. We changed from EV200 to Gigavac and had nothing
but problems .. This was in high voltage EV applications - must have used
more than 1000 units .. all had to go back .... it was a few years ago ...
so things may have changed ...

Strange thing was that application was fine ..all the Gigavac tech info
etc..was great .. but we keep getting welded contactor ... it was a very
expensive exercise, we will never use them again. Never had problem with
the EV200.

Yes the circuit saver on the EV200 can be noisy. But have not been a great
problem. Also can use the EV200 with no circuit saver and use a external
circuit saver ...

--


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
jluckey(at)pacbell.net
Guest





PostPosted: Wed Nov 20, 2013 3:34 pm    Post subject: Contactors Reply with quote

Eric,

As you know, the typical small experimental aircraft may typically have 2 contactors:
1. the "master" - continuous duty, usually rated for ~80 amps, typically handles < 40 amps
2. the starter solenoid - intermittent duty, rated for cranking 200-300 amps

For which of these missions are you suggesting the GX200?
Looks like a great device but seems to be overkill for these applications w/ a price to match.
-Jeff

From: Eric M. Jones <emjones(at)charter.net>
To: aeroelectric-list(at)matronics.com
Sent: Wednesday, November 20, 2013 2:07 PM
Subject: Contactors


--> AeroElectric-List message posted by: "Eric M. Jones" <emjones(at)charter.net (emjones(at)charter.net)>

We have discussed contactors for years and I have always recommended the Kilovac EV200 and the Gigavac GX11, but there is a new contactor available from Gigavac to compete directly with the Kilovac EV200 and offers some additional benefits, such as no noise, terminal shields, and improved performance characteristics. I was considering selling these, but there isn't any meat on the bone left after getting them from Gigavac.

I have one and I like these more than the Kilovacs.

Part Number Description  
GX200BB 350A, 12Vdc coil, 24" leads       1-4 $116
5-9 $104
10-24 $99

See: http://www.gigavac.com/pdf/ds/pp/gx200.pdf

(ignore their weird warning to see their other contactors (remember Gigavac is refering to 200A continuous). Gigavac is known for having strange marketing, but great products. Also ignore their manual switches...they are made for really, really, high-voltage applications and are much too big.

But I recommend the GX200 as the best contactor for the task, if you are planning to use a contactor at all.

--------
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net


Read this topic online here:

http://forums.matronics.com/viewtopic.php?p=413611#413611www.aeroelectric.com< * HomebuiltHELP www.mypilotstore.cbsp; -Matt Dralle, List Ad=================



[quote][b]


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
jluckey(at)pacbell.net
Guest





PostPosted: Wed Nov 20, 2013 3:37 pm    Post subject: Contactors Reply with quote

Eric,

As you know, the typical small experimental aircraft may typically have 2 contactors:
1. the "master" - continuous duty, usually rated for ~80 amps, typically handles < 40 amps
2. the starter solenoid - intermittent duty, rated for cranking 200-300 amps

For which of these missions are you suggesting the GX200?
Looks like a great device but seems to be overkill for these applications w/ a price to match.
-Jeff

From: Eric M. Jones <emjones(at)charter.net>
To: aeroelectric-list(at)matronics.com
Sent: Wednesday, November 20, 2013 2:07 PM
Subject: Contactors


--> AeroElectric-List message posted by: "Eric M. Jones" <emjones(at)charter.net (emjones(at)charter.net)>

We have discussed contactors for years and I have always recommended the Kilovac EV200 and the Gigavac GX11, but there is a new contactor available from Gigavac to compete directly with the Kilovac EV200 and offers some additional benefits, such as no noise, terminal shields, and improved performance characteristics. I was considering selling these, but there isn't any meat on the bone left after getting them from Gigavac.

I have one and I like these more than the Kilovacs.

Part Number Description  
GX200BB 350A, 12Vdc coil, 24" leads       1-4 $116
5-9 $104
10-24 $99

See: http://www.gigavac.com/pdf/ds/pp/gx200.pdf

(ignore their weird warning to see their other contactors (remember Gigavac is refering to 200A continuous). Gigavac is known for having strange marketing, but great products. Also ignore their manual switches...they are made for really, really, high-voltage applications and are much too big.

But I recommend the GX200 as the best contactor for the task, if you are planning to use a contactor at all.

--------
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net


Read this topic online here:

http://forums.matronics.com/viewtopic.php?p=413611#413611www.aeroelectric.com< * HomebuiltHELP www.mypilotstore.cbsp; -Matt Dralle, List Ad=================



[quote][b]


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Eric M. Jones



Joined: 10 Jan 2006
Posts: 565
Location: Massachusetts

PostPosted: Wed Nov 20, 2013 4:53 pm    Post subject: Re: Contactors Reply with quote

Jan,
Quote:

I hope they have improved. We changed from EV200 to Gigavac and had nothing but problems .. This was in high voltage EV applications - must have used more than 1000 units .. all had to go back .... it was a few years ago ...
so things may have changed ...


I have heard of problems with big contactors in EVs charging supercaps. Inless the caps are "pre-charged" or there is a line resistor, the current is ~infinite. These lessons were learned painfully in EVs. But Gigavac makes good stuff and they deserve a look. Gigavac makes scores of different contactors.

Jeff,

There are main battery contactors. Maybe more. They would be overkill for 40A.


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net
Back to top
View user's profile Send private message Send e-mail Visit poster's website
deej(at)deej.net
Guest





PostPosted: Wed Nov 20, 2013 5:26 pm    Post subject: Contactors Reply with quote

On Nov 20, 2013, at 5:07 PM, "Eric M. Jones" <emjones(at)charter.net> wrote:

Quote:

GX200BB 350A, 12Vdc coil, 24" leads 1-4 $116


This is not intended as a flame, and I am not trying to join the contactor war. Smile

I literally just received a starter contactor from Aircraft Spruce that cost $9.95, and I bought a pair of IN5402 diodes from Radio Shack for $1.99. The contactor on my Glastar is identical as far as I can tell, and has been working for the last 14 years even though it has no diode installed on it. Once this summer I pushed the button and did not get the "click" from the contactor and the starter did not turn. A few seconds later I pushed the button and it worked fine, and has worked fine for a few dozen starts since then. I'm replacing it "just because" and also because it is dirt cheap to do so.

Serious question, what benefit do I really get for that extra $104?

-Dj


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Eric M. Jones



Joined: 10 Jan 2006
Posts: 565
Location: Massachusetts

PostPosted: Wed Nov 20, 2013 5:55 pm    Post subject: Re: Contactors Reply with quote

Dj-

I don't want to crank out another bushel of words on this either (and I'm certain Bob N is tired of it), but:

The type 70 you used is position-sensitive, operates up to only 122 degF (!), is not airtight, water-tight not fuel-proof, and sucks current. Yes, it has been used for years, and it is cheap. Time to change.

ps, if you'd used bidirectional Zeners instead of p/n diodes, the contactor would probably still be working.

pps, I am a proponent of using NO contactors if you can arrange it. So that's where I stand. Check the PDF and if it suits your plans, try one.


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net
Back to top
View user's profile Send private message Send e-mail Visit poster's website
deej(at)deej.net
Guest





PostPosted: Wed Nov 20, 2013 6:49 pm    Post subject: Contactors Reply with quote

On 11/20/2013 8:55 PM, Eric M. Jones wrote:
Quote:

The type 70 you used is position-sensitive, operates up to only 122 degF (!), is not airtight, water-tight not fuel-proof, and sucks current. Yes, it has been used for years, and it is cheap. Time to change.

Hi Eric,
Thank you for responding. I don't really feel that answers my
question though, at least I don't think it answers it from my
perspective as a typical experimental guy on a budget. This email (and
the previous one) really isn't directed at you specifically, although I
suppose it might look that way.

Literally, what benefit do I really get for that extra $104? All I
want is to push the button and have the starter turn. At $9.95, the 14
year old contactor provided that for 71 cents per year. I do not
understand how the more expensive contactor is going to do the job any
better. Budget is a concern for me, so if I am looking at a $12
solution compared to a $116 solution, I really need to see some clear
benefits before I am willing to spend the extra money when they both
seem to do the same thing.

Having said all that, understand that I'm not an electronics
expert, and am unlikely to appreciate the finer nuances of the method of
how each of these types of contactors work. That is probably fairly
typical of most of the people on this list. The $116 contactor may save
a few amps of current, for example, but that really doesn't mean a lot
to me. I have a 20 ah battery, and I use the contactor for a few
seconds to start the engine, then the battery gets charged back up
during the flight. Whether it uses 1 amp versus 5 amps (made up numbers
for illustration), it doesn't really have an impact on how I use it, at
least in this case.

I live in New England, so 122F as a limit isn't a concern (-20F
might be! Smile ), and even a 10 minute turnaround for a fuel stop in the
summer so the cowling is still hot hasn't seemed to create any issues.
Airtight and watertight doesn't seem to matter since it is inside the
cowling and protected from the elements.

The one item that you mentioned, not being fuel proof, could be a
potential safety issue if somehow fuel were to be sprayed onto the
contactor and an internal spark when I push the button caused it to
ignite. It is pretty far away from my fuel system though, and I have a
gravity feed fuel setup, so very low pressure. The chances of fuel
getting to the contactor seems very slight even in the event of a fuel leak.

This email went on longer than I intended, but I thought it useful
to offer a perspective from someone that I think is a typical
representation of people on this list.

Quote:
ps, if you'd used bidirectional Zeners instead of p/n diodes, the contactor would probably still be working.

For clarity, the 14 year old contactor has never had diodes (or
zeners) installed on it, and it is still working. I don't really have
any reason to replace it except for that one blip a few months back, and
that I am completely re-doing a bunch of electrical items on the plane
and it is convenient to do it while I have everything apart. The new
one that I will be installing will get a diode across it. Maybe it will
last 28 years instead of only 14... Wink

I hope this email is taken in the positive spirit in which it is
intended. I mean no offense, and hope none is taken.

-Dj

--
Dj Merrill - N1JOV - VP EAA Chapter 87
Sportsman 2+2 Builder #7118 N421DJ - http://deej.net/sportsman/
Glastar Flyer N866RH - http://deej.net/glastar/


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Eric M. Jones



Joined: 10 Jan 2006
Posts: 565
Location: Massachusetts

PostPosted: Thu Nov 21, 2013 6:58 am    Post subject: Re: Contactors Reply with quote

Dj--
Quote:
Hi Eric,
Thank you for responding. I don't really feel that answers my
question though, at least I don't think it answers it from my
perspective as a typical experimental guy on a budget.


Flying is a pretty expensive sport no matter how you do it. But I don't encourage everyone to immediately change to the latest and greatest. If you are happy with what you have, then by reading this list and doing some investigation, you at least know what's available. If you want to build an aircraft to be a stellar example of wonderfulness, and aren't so concerned about budget, then different choices might apply.

Even Bob N's book and writings show "simple, more complicated, sophisticated" approaches and Z-diagrams. Over the years my aspirations have slipped from whiz-bang to much-simpler. For example I don't want a dual battery system, an inverted fuel system, and probably won't have an AOA either. I'll probably put off the autopilot for later.

As for the 122F spec limit, If your contactor is under-cowl, then it is a real limitation. Evidence seems to indicate that the modern type-70 is not the same device it was some years prior.

So what do you get for an additional $104? A lot better, safer, lower hold-current, higher-temp device. It makes sense in my checkbook, but might not in everyone's. But I am still aiming at a contactor-free simple design.

ps, I'm building a Glastar.
pps, The Gigavac and Kilovac designs use bidirectional Zeners as coil suppressors. Wonder why? Because the diodes recirculate the current and slow the opening of the armature, causing arcing; the bidirectional Zeners don't.


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net
Back to top
View user's profile Send private message Send e-mail Visit poster's website
jrevens(at)comcast.net
Guest





PostPosted: Thu Nov 21, 2013 8:59 am    Post subject: Contactors Reply with quote

Quote:
On 11/20/2013 Dj Merrill wrote: ”For clarity, the 14 year old contactor has never had diodes (or zeners) installed on it, and it is still working. I don't really have any reason to replace it except for that one blip a few months back, and that I am completely re-doing a bunch of electrical items on the plane and it is convenient to do it while I have everything apart. The new one that I will be installing will get a diode across it. Maybe it will last 28 years instead of only 14... Wink I just want to point out that the “blip” you experienced was very possibly caused by the switch controlling the contactor, not the contactor itself. A diode is usually installed to protect the switch contacts from excessive arcing, and not the contactor itself. I don’t believe that the diode will directly do anything to help the contactor have a longer life. John Evens
0





[quote][b]


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
jrevens(at)comcast.net
Guest





PostPosted: Thu Nov 21, 2013 9:11 am    Post subject: Contactors Reply with quote

Quote:
On 11/20/2013 Dj Merrill wrote: ”For clarity, the 14 year old contactor has never had diodes (or zeners) installed on it, and it is still working. I don't really have any reason to replace it except for that one blip a few months back,and that I am completely re-doing a bunch of electrical items on theplane and it is convenient to do it while I have everything apart.The new one that I will be installing will get a diode across it.Maybe it will last 28 years instead of only 14... Wink
0
Quote:
1
Quote:
2
Quote:
3
Quote:
4
Quote:
5
Quote:
6
Quote:
7
Quote:
8






No virus found in this message.
Checked by AVG - www.avg.com
11/20/13 [quote][b]


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
nuckolls.bob(at)aeroelect
Guest





PostPosted: Thu Nov 21, 2013 10:03 am    Post subject: Contactors Reply with quote

As for the 122F spec limit, If your contactor is under-cowl, then it
is a real limitation. Evidence seems to indicate that the modern
type-70 is not the same device it was some years prior.

And in what way are these 'differences' a step-down
from what was done in the past?

Please do not side-step this question Eric. In what
way have you discovered that the modern incarnation
of the 70-series contactor is inferior to that which
first flew on the C140 in 1948 or any other era in
between?

Published temp limits are founded in the outcome of an
MTBF study where operating temperature strongly influences
service life of organics (insulation and molded
bobbins). A 70-series contactor on a golf-cart
or fork-lift is subject to 100x the service-stress of a
battery contactor in a light airplane. The question
to be asked and answered is assuming that a 70-series
device at 122F is good for xx,xxx operations at
full switching load and 122F, how badly does that
xx,xxx number degrade at say . . . 160F?
So what do you get for an additional $104? A lot better, safer, lower
hold-current, higher-temp device. It makes sense in my checkbook, but
might not in everyone's.

Quantify 'better' and 'safer' . . . cite any instances
where failure-to-perform by a 70 series contactor has
presented anything other than a maintenance event.

Cite also the outcome of a failure mode effects analysis
that should the demonstrably low probability contactor
failure actually happen in flight. Have you deduced
a heretofore unidentified risk to airframe/people in
an airplane fitted with an e-bus?

But I am still aiming at a contactor-free simple design.

No problem. Lamar offers a line of all solid state
contactors which they say are suited to both
battery and starter control. Aircraft Spruce
offers them right now.

http://tinyurl.com/or73cxr

pps, The Gigavac and Kilovac designs use bidirectional Zeners as coil
suppressors. Wonder why? Because the diodes recirculate the current
and slow the opening of the armature, causing arcing; the
bidirectional Zeners don't.

I proved this assertion incorrect some years back on
the bench. The plain vanilla diode does extend operating
delay but has no measurable effect on transition velocity
(arcing). The operating delay is on the order of milliseconds
and transparent to the pilot and ship's systems.

Consider Figures 5 thru 8 of this document.

http://tinyurl.com/36783n7

Particularly the arc signature of a spreading relay
contact where (1) the coil is not suppressed in any
way and (2) suppressed with a plain vanilla diode.

If this document is in error, I need to know. Help
me out . . .

Consider this article published in the Cessna 120/140
Forum. http://tinyurl.com/oe2m52v

Here the author claims to have measured the effects of
coil spikes induced directly onto the bus of his
C182. He cites some startling numbers . . .

We have discovered through simple bench tests and rudimentary
logic that 99.99% of the energy from a collapsing contactor/relay
coil is expended across the contacts of the controlling
switch . . . that in fact, the energy does not propagate out
onto the system. It would be nice if he had published
a wiring diagram for his experiment so that it could
be repeated.

Eric, if your wish is to be a persuasive teacher,
you're going to have to bring your science to
the discussion. If you have evidence that argues with my
deductions, nobody would be happier than I to know that
what I've been teaching is in error.
Bob . . .

////
(o o)
===========o00o=(_)=o00o=========
< Go ahead, make my day . . . >
< show me where I'm wrong. >
=================================


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
jan(at)CLAVER.DEMON.CO.UK
Guest





PostPosted: Thu Nov 21, 2013 10:43 am    Post subject: Contactors Reply with quote

Hi Jeff,

I am well aware of the issue around pre-charging of capacitors. That is
bread and butter stuff to anyone involved in the EV industry or dealing with
any systems that have large capacitors ...

What was so frustrating in our experience was that what Gigavac was
proposing as an alternative to the EV200 ... all looked right on paper ..
but did not work in our application ... the EV200 did .. and still do. More
frustrating was the Gigavac was not able to come up with a answer to the
problem. He we had to pull them all. And re-fit EV200 ...

Anyway ... as a starter or main contactor on a light aircraft ... Well .. I
have no further comment to add.

Jan

--


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Eric M. Jones



Joined: 10 Jan 2006
Posts: 565
Location: Massachusetts

PostPosted: Thu Nov 21, 2013 1:31 pm    Post subject: Re: Contactors Reply with quote

It would be nice to have gotten an answer from Gigavac. I'll contact them and try to dig up what happened.

- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net
Back to top
View user's profile Send private message Send e-mail Visit poster's website
nuckolls.bob(at)aeroelect
Guest





PostPosted: Thu Nov 21, 2013 1:45 pm    Post subject: Contactors Reply with quote

I just want to point out that the "blip" you experienced was very possibly
caused by the switch controlling the contactor, not the contactor itself.
A diode is usually installed to protect the switch contacts from excessive
arcing, and not the contactor itself. I don't believe that the diode will
directly do anything to help the contactor have a longer life.

John Evens

AGREED!

Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Eric M. Jones



Joined: 10 Jan 2006
Posts: 565
Location: Massachusetts

PostPosted: Thu Nov 21, 2013 2:14 pm    Post subject: Re: Contactors Reply with quote

EMJ said-As for the 122F spec limit, If your contactor is under-cowl, then it
is a real limitation. Evidence seems to indicate that the modern
type-70 is not the same device it was some years prior.

Quote:
And in what way are these 'differences' a step-down
from what was done in the past?

Please do not side-step this question Eric. In what way have you discovered that the modern incarnation of the 70-series contactor is inferior to that which first flew on the C140 in 1948 or any other era in between?


The photo you showed of the type-70 with the red RTV seal. I haven't opened many type-70s. In 1948 they probably had phenolic bobbins, now they have nylon bobbins.

Quote:
Published temp limits are founded in the outcome of an
MTBF study where operating temperature strongly influences
service life of organics (insulation and molded
bobbins). A 70-series contactor on a golf-cart
or fork-lift is subject to 100x the service-stress of a
battery contactor in a light airplane. The question
to be asked and answered is assuming that a 70-series
device at 122F is good for xx,xxx operations at
full switching load and 122F, how badly does that
xx,xxx number degrade at say . . . 160F?


The historical engineering data is not available for the type 70. I have tried. All we can go by is the published specifications. Why does this bother you?

So what do you get for an additional $104? A lot better, safer, lower
hold-current, higher-temp device. It makes sense in my checkbook, but
might not in everyone's.

Quote:
Quantify 'better' and 'safer' . . . cite any instances where failure-to-perform by a 70 series contactor has presented anything other than a maintenance event.


Better and safer means higher temp and fuel proof....for a start. Previously I published a comparison of the type-70 with the EV200. Maybe I'll do it again.

Quote:
Cite also the outcome of a failure mode effects analysis that should the demonstrably low probability contactor failure actually happen in flight. Have you deduced a heretofore unidentified risk to airframe/people in
an airplane fitted with an e-bus?


Sounds too much like a waste of time for anyone whose mind is made up. The 122F limit is enough to have it put on the Do Not Use List.

But I am still aiming at a contactor-free simple design.

Quote:
No problem. Lamar offers a line of all solid state contactors which they say are suited to both battery and starter control. Aircraft Spruce
offers them right now.

pps, The Gigavac and Kilovac designs use bidirectional Zeners as coil
suppressors. Wonder why? Because the diodes recirculate the current
and slow the opening of the armature, causing arcing; the
bidirectional Zeners don't.

Quote:
I proved this assertion incorrect some years back on the bench. The plain vanilla diode does extend operating delay but has no measurable effect on transition velocity (arcing). The operating delay is on the order of milliseconds
and transparent to the pilot and ship's systems.

Consider Figures 5 thru 8 of this document.
Particularly the arc signature of a spreading relay contact where (1) the coil is not suppressed in anyway and (2) suppressed with a plain vanilla diode.

If this document is in error, I need to know. Help me out . . .


At the time I didn't like your test. I won't dig it up now. Sometimes just doing the best engineering approach is the logical thing to do. Since you know using a p/n diode SLOWS the contactor opening and causes arcing...why would you do that?

Quote:
Consider this article published in the Cessna 120/140
Forum. http://tinyurl.com/oe2m52v

Here the author claims to have measured the effects of
coil spikes induced directly onto the bus of his
C182. He cites some startling numbers . . .

We have discovered through simple bench tests and rudimentary
logic that 99.99% of the energy from a collapsing contactor/relay
coil is expended across the contacts of the controlling
switch . . . that in fact, the energy does not propagate out
onto the system. It would be nice if he had published
a wiring diagram for his experiment so that it could
be repeated.


The article has some issues which I will answer later. The key problem is that neither he nor you seem to understand why a bidirectional zener is far better to use in coil suppression service, and what it does that a diode does not do. NOBODY makes a commercial contactor that uses a p/n diode for coil suppression for good reasons. NOBODY. The sine qua non of coil suppression is to reduce the opening time. I don't think everyone ought to tear out the parts and replace them, but when buiding a system from scratch, why not do the right thing?

If you want to claim the wrong way is "good enough", okay.

Quote:
Eric, if your wish is to be a persuasive teacher, you're going to have to bring your science to the discussion. If you have evidence that argues with my
deductions, nobody would be happier than I to know that what I've been teaching is in error.
Bob . . .


No, you wouldn't. But I respect your work.


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Eric M. Jones
www.PerihelionDesign.com
113 Brentwood Drive
Southbridge, MA 01550
(508) 764-2072
emjones(at)charter.net
Back to top
View user's profile Send private message Send e-mail Visit poster's website
nuckolls.bob(at)aeroelect
Guest





PostPosted: Thu Nov 21, 2013 5:58 pm    Post subject: Contactors Reply with quote

The photo you showed of the type-70 with the red RTV seal. I haven't
opened many type-70s. In 1948 they probably had phenolic bobbins, now
they have nylon bobbins.

Yes. Ownership and marketing of the 70-series devices
has changed several times over the years. Most certainly,
they have benefited from a host of changes that were either
(1) consistent with processes and materials of the new
owners and/or (2) process and materials improvements
that did not degrade original design goals.

It's easy to fall into the 'trap' for taking notice
of new, faster, cheaper or convenient changes and translate
them into some nefarious or incompetent decision to reduce costs
while sacrificing original design goals. The cars we all
drive are much cheaper than machines we used to purchase
50 years ago yet they come with more features and longer
service lives. Your notice of historical variation in
design as a driver for safety and reliability is without
foundation.

No doubt this DOES happen but I challenge any notion
that the present incarnation of the 70-series contactor
is in any way a poorer return on investment than it was
in 1949.

The historical engineering data is not available for the type 70. I
have tried. All we can go by is the published specifications. Why
does this bother you?

It doesn't bother me in the least. How did a lack of
historical data offered by manufacturers become a solid
foundation for declaring a product of poor value and an
operational hazard? I don't know much about the internal
decisions that produced the cars I drive either . . . but
no way would I spend the same money in 2013 dollars for
a 1960's automobile as a point A to point B transportation
machine. Given the service life and features of the last
5 cars I've owned I can confidently assert that cheaper
is better.

Better and safer means higher temp and fuel proof....for a start.
Previously I published a comparison of the type-70 with the EV200.
Maybe I'll do it again.

I didn't see that. Was it published here on the AeroElectric
List? I'd like to read it. But if it's simply a tit-for-tat
listing of features on the promotional literature, be sure
to explain how the lack of some new feature posed
a risk to cost of ownership or safety.

>Cite also the outcome of a failure mode effects analysis that
should the demonstrably
>low probability contactor failure actually happen in flight. Have
>you deduced a heretofore unidentified risk to airframe/people in an
>airplane fitted with an e-bus?

Sounds too much like a waste of time for anyone whose mind is made
up. The 122F limit is enough to have it put on the Do Not Use List.

Waste of time? How so? If your assertion is that I preach
the gospel of bad science, poor design goals and risky
decisions based on bad science, then I must be a menace to
children and other living things. What is the science upon
which your opinion is based? My mind is not 'made up' . . .
show me (or more important - the members of this List)
where I'm wrong. I don't write for you and I don't ask you
to write for me . . . do it for the membership of this List.

At the time I didn't like your test. I won't dig it up now. Sometimes
just doing the best engineering approach is the logical thing to do.
Since you know using a p/n diode SLOWS the contactor opening and
causes arcing...why would you do that?

How do I KNOW that? Can you do an experiment
on the bench that demonstrates it? If you didn't
like my test then, why did you let it slide?

The article has some issues which I will answer later. The key
problem is that neither he nor you seem to understand why a
bidirectional zener is far better to use in coil suppression
service, and what it does that a diode does not do. NOBODY makes a
commercial contactor that uses a p/n diode for coil suppression for
good reasons. NOBODY. The sine qua non of coil suppression is to
reduce the opening time. I don't think everyone ought to tear out the
parts and replace them, but when buiding a system from scratch, why
not do the right thing?

Really? How about the S701 series starter contactors
I sold for years with a plain vanilla diode factory
installed? How about the fact that plain vanilla
diodes have been installed on the Cessna single
engine products for decades . . . with no overt
demonstrations of bad engineering? I aware of no
contactors with factory installed, zener based
coil suppression . . . lots of devices are sold with
plain vanilla diodes.

Small relays are offered with bi-directional devices
so that the system designer can use them in both
simple power management -and- controls where drop
out delay could become an issue.
If you want to claim the wrong way is "good enough", okay.

> Eric, if your wish is to be a persuasive teacher, you're going to
have to bring your science to the discussion. If you have evidence
that argues with my
> deductions, nobody would be happier than I to know that what I've
been teaching is in error.
> Bob . . .

No, you wouldn't. But I respect your work.

You respect my work but I'm lying? Okay Eric. I think
this conversation is over. Until such time that you
conduct and publish the outcome of demonstrations that
argue with what I have published and defended, you are
asked to keep your opinions on contactors off this List.
Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Fred Klein



Joined: 26 Mar 2012
Posts: 503

PostPosted: Fri Nov 22, 2013 1:36 pm    Post subject: Contactors Reply with quote

I confess to confusion about the need for a separate starter contactor...one which would substitute for a solenoid built into the starter.

What I don't understand in particular is that w/ my Subaru starter (with solenoid)...which seems to be a durable and robust combination with a trouble-free history in the automotive industry...what is gained by a separate starter contactor?

I will still have a hot wire from my rear battery to my firewall...(which is where I would mount such a separate contactor)...so all I gain is a 3 foot length of "not hot" wire from my (superfluous?) contactor connecting to the starter solenoid...and this same length of wire would become "not hot" immediately after I kill the master contactor.

What am I missing here?

Fred


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
View user's profile Send private message
nuckolls.bob(at)aeroelect
Guest





PostPosted: Fri Nov 22, 2013 2:23 pm    Post subject: Contactors Reply with quote

Quote:
What am I missing here?

See:
http://tinyurl.com/op5cs2g

Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Fred Klein



Joined: 26 Mar 2012
Posts: 503

PostPosted: Fri Nov 22, 2013 4:01 pm    Post subject: Contactors Reply with quote

Thank you...I'm on it...F.

On Nov 22, 2013, at 2:22 PM, Robert L. Nuckolls, III wrote:

Quote:



> What am I missing here?

See:


http://tinyurl.com/op5cs2g



Bob . . .





- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> AeroElectric-List All times are GMT - 8 Hours
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group